Quote:
Originally Posted by Koppster
Hope you have better luck than I did. The dealer cleaned my sail switch and then it failed again so I cleaned it. Got about two more nights out of it and it failed again. I called the dealer, they warrantied the switch and let me change it out myself which saved me from having to tow the trailer in.
|
For brevity, I left out the sail switch test I performed. First, when I cleaned it, I focused on jetting canned air down into the switch to dislodge any grime that might have snuck into the switch components. These are NOT fancy, sealed switches. They are simple and cheap, and they live in an inherently dirty environment. Then I used an "electronics spray cleaner" to wash it. It is just a simple "plunger switch" that is "normally open" [off] when the fan isn't running on the furnace. When you push the plunger [button] the switch "closes" [turns on]. The cleaning efforts gave me a reliable switch.
I used a multi-meter with alligator clips to test the switch function after I cleaned it. With the multi-meter attached in "resistance" [ohms] mode, I tested "continuity." I repeatedly operated the switch to ensure that it was making a good, reliable connection. In my case, I was lucky, and the switch performed flawlessly.
To be honest, the switch seemed fine to begin with, but since I didn't test it prior to cleaning, I don't really know. The real solution may have been to cycle the power/reset switch.
As I understand it, the power/reset switch functions somewhat like the reset switch on a common power strip. If you overload the power strip, you must "cycle" [switch off then on] the switch, and it "resets" the power strip. The "mystery" is why the circulator fan will run, but the rest is shut off. I have not researched that, but many who guided me recommended cycling the power/reset switch, so I did.
So, if you cycle your power/reset switch on the furnace, I recommend that you cycle it about 5 to 10 times. It, too, may be a bit dusty inside, and by cycling it multiple times, you may improve the contacts connection when the switch is closed [on].
This whole process is a bit like "kicking it" or shaking it to make it work. These are not definitive fixes. But if you've ever dealt with a scratchy volume control on an old radio, you know that if you vigorously (even violently
) operate the volume control, it will dramatically improve the contacts on the (likely) rheostat and make the change in volume far less scratchy. That's kind of the principle involved here.
If all else fails, and if you test the switches and discover they are unreliable or failed, you'll need to replace them.
And then there's the matter of all the other things that can go wrong, from the circuit board (which on mine sits out in harm's way), thermostat, and so on. Any one of these can fail. But the smart money is on the sail switch and power/reset switch. Only after checking them would I move on to other possible failures.
Finally, you must pull the furnace (or have an outside access panel - lucky you) to service the sail switch. But make note of the location of the power/reset switch. It's likely that you can reach it and cycle it without removing the furnace. That might come in handy some night at 3 AM in October when your furnace won't start. Just sayin'.