If it were me I would first check the tightness of all connections inside your transfer switch. This is done WITH NO POWER APPLIED. Then, if you are comfortable measuring 120 volts with a volt meter, place the meter leads across the input wires from the power cord inside the transfer switch. This will measure the power coming in from your power cord.
If you plug in and there is no voltage showing on the meter, the problem is with your power cord be it in the cord or the prong connections. If the voltage is measured at the input of the transfer switch but the switch doesn't switch over, the problem most likely is the transfer switch.
You mentioned it happens on either 30 amp or 50 amp. Do you have 50 amp service and using a 30 amp adapter or do you have 30 amp service and using a 50 amp adapter? Just curious. It doesn't really make a big difference as the adapter is just basically tying connections together for input.