Expert A/C help needed

Need a sanity check.

Background:

10 day trip to South Dakota (amazing but hot). On the last day, front ac (Mach 15 on 2020 precept) dies. I was running on the generator on the way home. Breaker trips on generator. Reset. Fan runs. No Cold air.

Check everything with a volt meter. Fan and start Capacitors good. Thermostat inputs to control board. Good. Control board out. Good. Compressor and relay good. Assume I lost coolant. Call dealer. 16 weeks. Buy new ac unit because i want to camp this summer. Install new unit through acts of courage and strength. New unit doesn’t have new control boards… really. (old unit had the main control and the temperature control board). Put old control board on new unit. The temperature control board doesn’t seem to be needed on the new unit. Wired directly (like back ac into the compressor). No cold air !!

Double check everything. Swap back ac control board to front. Nothing. Put front board to the back unit. Back ac runs like a champ with the control board. So it’s good.

Swap both freeze thermocouples. All good. Both power up the back.

Check the breakers. All good. Double check the generator and try to run on it without shore power. Same results. Fan yes. Cold air not.

The compressor gets hot. But the coolant line doesn’t get cold.

Did I get a lemon or am I missing something. I’ve checked every circuit I can think of.
apgarrett is offline   Reply With Quote
Old 07-30-2022, 08:13 PM   #2
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,224
Do have a clamp on amp meter? Room to put it on the ac power line at the compressor to see if any current is flowing right when you turn unit on.
RPR is offline   Reply With Quote
Old 07-30-2022, 08:21 PM   #3
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
I can put my fluke meter on and hold it. No issues there.

Where would I put it it on the compressor? There are the three poles.

Tell me what you are thinking.
apgarrett is offline   Reply With Quote
Old 07-30-2022, 08:26 PM   #4
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,224
You may have voltage but no current flow. Seeing if and how much current(amps) the compressor is drawing.
RPR is offline   Reply With Quote
Old 07-30-2022, 08:52 PM   #5
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
Quote:
Originally Posted by RPR View Post
You may have voltage but no current flow. Seeing if and how much current(amps) the compressor is drawing.
Ok. I’ll check it tomorrow. I’m assuming from the capacitor to the compressor.
apgarrett is offline   Reply With Quote
Old 07-31-2022, 06:09 AM   #6
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
Zero amps out of the start capacitor to compressor.

Not sure why.
apgarrett is offline   Reply With Quote
Old 07-31-2022, 06:39 AM   #7
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
Never mind. Bad fuse in meter. I did have current. I just need to step away from this. I’m making bone head mistakes.

So frustrating. I feel like I missing something simple, but I’m starting to think I got a lemon.
apgarrett is offline   Reply With Quote
Old 07-31-2022, 06:53 AM   #8
Member
 
Join Date: May 2022
Location: Sonoma County
Posts: 61
There will not be an amp reading on the start compressor wire try another wire. On the compressor there will be two copper tubes one bigger than the other the smaller on will be HOT to the touch and the other cold under normal conditions indicating the compressor is pumping refrigerant. The amp reading will tell you if the motor is running or take a screw driver hold the end on the compressor body the other end of the driver hold to your ear and you will hear the motor running. If your compressor running and the small tube on the compressor is not hot chance’s are it is short or out of refrigerant.
Gary207 is offline   Reply With Quote
Old 07-31-2022, 09:49 AM   #9
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
Compressor is running. Confirmed by amps, humming, and the screw driver test.

I got a lemon. Thanks for the tips.
apgarrett is offline   Reply With Quote
Old 07-31-2022, 11:17 AM   #10
Senior Member
 
Join Date: Jun 2016
Location: Denver
Posts: 4,250
Quote:
Originally Posted by apgarrett View Post
Compressor is running. Confirmed by amps, humming, and the screw driver test.

I got a lemon. Thanks for the tips.

My Mach 15 leaked out all of it's refrigerant after a couple of years. I don't think the quality is in those units, that I'd expect.
__________________
2016 Greyhawk 31FK
pconroy is offline   Reply With Quote
Old 07-31-2022, 11:25 AM   #11
Senior Member
 
Join Date: Jun 2016
Location: Newburgh
Posts: 6,307
Just want to know how you confirmed the caps are good? Did you meter and read Mf's? I've seen many instances where someone will assume a good capacitor but not actually verify micro farrads.
__________________

2022 33RBTS
Progressive Industries EMS - Hardwired
Equalizer 4 Point WDH
2021 Ford F350 7.3
Air Lift Rear Bags w/ On Board Compressor (Pending)
2016 28BHBE - (Traded and Missed already)
Marcm157 is offline   Reply With Quote
Old 07-31-2022, 01:42 PM   #12
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
I checked them with my meter.
apgarrett is offline   Reply With Quote
Old 07-31-2022, 02:11 PM   #13
Member
 
Join Date: Jul 2017
Location: Jersey Shore
Posts: 68
2018 Jayco Precept 35s - my main AC unit is doing the same thing, trying to troubleshoot and have an onsite service appointment set for 8/10...hope you find out what's happening.
GerryB54 is offline   Reply With Quote
Old 07-31-2022, 02:26 PM   #14
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,224
Search the web and info on why possibility the capacitor could be the problem.
RPR is offline   Reply With Quote
Old 07-31-2022, 02:44 PM   #15
Senior Member
 
Join Date: Jun 2016
Location: Denver
Posts: 4,250
Quote:
Originally Posted by GerryB54 View Post
2018 Jayco Precept 35s - my main AC unit is doing the same thing, trying to troubleshoot and have an onsite service appointment set for 8/10...hope you find out what's happening.

I hope your outcome was better than mine. I replaced the caps, and everything tested fine. In the end, the only thing left was "no refrigerant"
__________________
2016 Greyhawk 31FK
pconroy is offline   Reply With Quote
Old 07-31-2022, 02:51 PM   #16
Senior Member
 
Join Date: Jun 2018
Location: VULCAN
Posts: 697
Quote:
Originally Posted by pconroy View Post
I hope your outcome was better than mine. I replaced the caps, and everything tested fine. In the end, the only thing left was "no refrigerant"
I have no idea why the AC manufacturers don't put ports on these units. The cost seems like it would be minimal.
__________________
2019 Ram 2500 Cummins

2022 Jayco 28.5 RSTS
Yooper906 is offline   Reply With Quote
Old 07-31-2022, 08:40 PM   #17
Member
 
Join Date: Jul 2021
Location: fishers
Posts: 76
Quote:
Originally Posted by Yooper906 View Post
I have no idea why the AC manufacturers don't put ports on these units. The cost seems like it would be minimal.
Money I suppose. Really frustrating how much time I’ve spent on this. I’ve asked for a refund and ordered an Atwood air commander. I’m sure it will have its issues too, but I have no faith in the Coleman units right now.
apgarrett is offline   Reply With Quote
Old 07-31-2022, 09:05 PM   #18
Member
 
Join Date: May 2022
Location: Sonoma County
Posts: 61
They do make clamp on access valves. Sup o 3in one refrigerant access valves is one brand. They also make an additive to stop a refrigerant leak you add to the system.
Gary207 is offline   Reply With Quote
Old 08-06-2022, 12:15 PM   #19
Junior Member
 
Join Date: May 2020
Location: DeLand
Posts: 11
Similar problems, but solved

Had the same with our 2021 Precept. Ended up changing out the front AC. Here are few hints to look at, without getting on the roof. You can check the compressor current from inside at the control box. Pull back the green wire mesh and put the clamp meter on the purple wire. A good operating system will indicate between 12 to 14 Amps. A unit that has lost the charge will show about 4 to 4.25 amps.


I did find the leak and to my surprise the case of the compressor had a micro hole in it. Pure and simple bad material selection by Tecumseh.



I was able to effect a repair, install service ports, evacuate and recharge to specs.



Down side is I did replace the unit, and now have a spare.



Did not replace with a Coleman. Went with a Haughton roof unit. Doesn't use a remote thermostat has all the necessary parts built in and uses a remote control. Quieter and a lot more efficient.



At its best the Coleman would only get a delta temp difference of 19 to 21 Degrees, Where the Hauhton is averaging 28 to 30. Supposedly has a built in soft-start, But I cant confirm this. Quite pleased and I'll also mention about 400 bucks less expensive.


As always IMHO
JohnH is offline   Reply With Quote
Old 08-08-2022, 06:15 AM   #20
Junior Member
 
Join Date: Jun 2020
Location: Milton
Posts: 9
Our 2018 Jayco Precept 29v had the same issue with our front A/C. Started not working right at the 2 year mark, I had probably used it less than 40 times. Due to my lack of trust at the dealership we purchased it at who said the whole unit needed to be replaced and that neither they or Jayco would honor the 2 year warranty as I was 1 month beyond the 2 years I found a local RV repairman who diagnosed and replaced the A/C? heat pump and $2400 later I have a working unit.
Brian
Bsenecal is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:02 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.