A/C 20 Amp breaker tripping

This is a relatively recent development for my 2017 Greyhawk 29 MV. The 20 amp A/C breaker trips after running about 20-30 minutes. Replacing the breaker had no effect. Upon closer inspection, all of the breakers are super hot. My quick fix wax to station a small fan next to the open breaker compartment. This worked and I can run the A/C as long as I want without tripping the breaker. Obviously, this is nothing more than a temporary, quick fix. I noticed that the compartment fan has never come on, but since that’s associated with the inverter, it should have no bearing on the breakers. Is the only remaining cause a bad A/C unit?
jramsey2008 is offline   Reply With Quote
Old 07-31-2022, 02:40 PM   #2
Senior Member
 
Join Date: Jun 2016
Location: Denver
Posts: 4,250
Quote:
Originally Posted by jramsey2008 View Post
all of the breakers are super hot

Not good!


Loose connections in any of them? Or are you saying the breakers stay cool, unless the AC runs and then all the breakers get hot?
__________________
2016 Greyhawk 31FK
pconroy is offline   Reply With Quote
Old 07-31-2022, 02:53 PM   #3
Senior Member
 
Scoutmaster253's Avatar
 
Join Date: Apr 2018
Location: Ravenna
Posts: 417
Quote:
Originally Posted by jramsey2008 View Post
This is a relatively recent development for my 2017 Greyhawk 29 MV. The 20 amp A/C breaker trips after running about 20-30 minutes. Replacing the breaker had no effect. Upon closer inspection, all of the breakers are super hot. My quick fix wax to station a small fan next to the open breaker compartment. This worked and I can run the A/C as long as I want without tripping the breaker. Obviously, this is nothing more than a temporary, quick fix. I noticed that the compartment fan has never come on, but since that’s associated with the inverter, it should have no bearing on the breakers. Is the only remaining cause a bad A/C unit?
What is your inside and outside air temp?
__________________
2014 Greyhawk 31FS
RV's, Pop-ups, and Tents going back to the 1960's
Scoutmaster253 is offline   Reply With Quote
Old 07-31-2022, 03:21 PM   #4
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
Hot breakers

I know the connections on the A/C breaker (20/15 combo) are tight, as replacing that breaker was my first step. When the new breaker tripped I noticed that all were hot. I’ll be replacing the single 15 amp breaker tomorrow (it seemed to be the hottest, though that could just be my imagination), and will recheck all connections then.
jramsey2008 is offline   Reply With Quote
Old 07-31-2022, 03:26 PM   #5
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
I’ll also check the breakers before the A/C comes on to verify one way or the other if that circuit alone is causing the problem.
jramsey2008 is offline   Reply With Quote
Old 07-31-2022, 03:27 PM   #6
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
Outside 92-94. Inside, 79.
jramsey2008 is offline   Reply With Quote
Old 07-31-2022, 03:33 PM   #7
RPR
Senior Member
 
Join Date: Dec 2018
Location: Owens Cross Roads
Posts: 3,224
Is your power cord from the pedestal getting hot? This heat is may be taxing the campground capability.
RPR is offline   Reply With Quote
Old 07-31-2022, 03:45 PM   #8
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
The power cord temp is fine. These temps in Florida are normal for this time of year and we didn’t experience anything like this last year.
jramsey2008 is offline   Reply With Quote
Old 07-31-2022, 05:18 PM   #9
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 3,600
I would check and make sure you are not encountering low voltage. ~CA
__________________
2010 GreyHawk 31SS
craigav is offline   Reply With Quote
Old 07-31-2022, 06:30 PM   #10
Senior Member
 
Jerry713's Avatar
 
Join Date: Jul 2022
Location: Elgin
Posts: 881
I had this problem once and ended up having to replace the power distribution/converter system.

I wouldn't step over a dollar to try and save a dime here. You could be looking at a fire hazard. Might be worth 120 bucks or so having a mobile RV tech check it out if you're not sure what the issue is.

I've seen one burn to the ground because of some sort of electrical issue with the power distribution system.
Jerry713 is offline   Reply With Quote
Old 07-31-2022, 06:46 PM   #11
Senior Member
 
JimD's Avatar
 
Join Date: Apr 2017
Location: Inland Empire, California
Posts: 2,006
Current flowing through a resistance will generate heat. If there is nothing running on a breaker it can not generate any heat. Therefore the heat must be coming from the high current draw of the AC.

I am not familiar with your power distribution center but can only surmise as to how it is set up. I would make sure the buss bar the breaker is connected to is bright and shiny where the breaker grabs it. Same thing for the main breaker(s) on the panel. If that is loose or corroded it will generate heat which will saturate the internals of the center. The current will be flowing in from the power line, through the main breaker(s), through the buss bar, and then through the AC breaker. Any resistance in that circuit could cause heat.

Also, make sure the neutral connections are all tight. The return is often overlooked in electrical problems.

With the center cool before you energize the AC, try turning on the AC while trying to see where the heat is coming from before everything is hot.

I agree with all that say this could be a dangerous situation.
__________________


Jim

Retired electronic technician (45 years in the field)
2017 Greyhawk 29W (solar & many other mods)
wife (maybe I should have given her top billing)
JimD is offline   Reply With Quote
Old 08-06-2022, 08:34 AM   #12
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
Follow-up on A/C breaker tripping

I had an RV A/C technician out to test the system. The A/C pulls 17 amps on a 20 amp circuit. Nothing else out of the ordinary was found, other than he questioned why the inverter fan appeared inoperable. With the heat spell we've been having, continuous running of the A/C was viewed as the cause of the circuit breaker heating up and causing it to trip, i.e., the circuit is not robust enough to handle continuous operation over a long stretch of time. Using a small portable fan to cool the breakers works and was considered by the technician to be a reasonable solution during the heat wave.
jramsey2008 is offline   Reply With Quote
Old 08-06-2022, 09:59 AM   #13
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 3,600
Quote:
Originally Posted by jramsey2008 View Post
I had an RV A/C technician out to test the system. The A/C pulls 17 amps on a 20 amp circuit. Nothing else out of the ordinary was found, other than he questioned why the inverter fan appeared inoperable. With the heat spell we've been having, continuous running of the A/C was viewed as the cause of the circuit breaker heating up and causing it to trip, i.e., the circuit is not robust enough to handle continuous operation over a long stretch of time. Using a small portable fan to cool the breakers works and was considered by the technician to be a reasonable solution during the heat wave.
Earlier you mentioned the ambient temp outside was in the low to mid 90's, did the A/C technician tell you that pulling 17a was normal for your A/C? I don't know which A/C you have, however it is not normal to pull that many amps for a 15k btu A/C, in fact a 20a breaker is designed to trip at 80% of its rated load for a continuous load which is 3 hours. In other words, a 20a breaker will trip at anything above 16a with time, and the time is less and less as you exceed the 16a (80%). My 15k A/C is older than yours, likely less efficient and runs 14~15a even with temps 105+, so something is still not right with your setup, could be low voltage as I mentioned earlier, did the tech tell you what the voltage was when the A/C is running and pulling 17a? ~CA
__________________
2010 GreyHawk 31SS
craigav is offline   Reply With Quote
Old 08-06-2022, 03:38 PM   #14
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
Quote:
Originally Posted by craigav View Post
Earlier you mentioned the ambient temp outside was in the low to mid 90's, did the A/C technician tell you that pulling 17a was normal for your A/C? I don't know which A/C you have, however it is not normal to pull that many amps for a 15k btu A/C, in fact a 20a breaker is designed to trip at 80% of its rated load for a continuous load which is 3 hours. In other words, a 20a breaker will trip at anything above 16a with time, and the time is less and less as you exceed the 16a (80%). My 15k A/C is older than yours, likely less efficient and runs 14~15a even with temps 105+, so something is still not right with your setup, could be low voltage as I mentioned earlier, did the tech tell you what the voltage was when the A/C is running and pulling 17a? ~CA
The tech didn’t think 17 amps was a problem, but you’re probably right. We stayed in Yuma a couple years back and ran the A/C nonstop during 105 degree outside temperature without tripping the breaker (the A/C wasn’t up to the task either, as the inside temp rose into the low 90s). He didn’t report the voltage, but I would be surprised if it was low, as we’re in a big resort operating at 1/3 occupancy and we have our own connection to the electric company. I’m guessing the unit is worn out and needs to be replaced.
jramsey2008 is offline   Reply With Quote
Old 08-06-2022, 08:03 PM   #15
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 3,600
Quote:
Originally Posted by jramsey2008 View Post
The tech didn’t think 17 amps was a problem, but you’re probably right. We stayed in Yuma a couple years back and ran the A/C nonstop during 105 degree outside temperature without tripping the breaker (the A/C wasn’t up to the task either, as the inside temp rose into the low 90s). He didn’t report the voltage, but I would be surprised if it was low, as we’re in a big resort operating at 1/3 occupancy and we have our own connection to the electric company. I’m guessing the unit is worn out and needs to be replaced.
The compressor pulling 17 amp is a bit high for sure. The most common reason for an A/C compressor to be pulling higher amps than expected (other than low voltage, or very dirty coils, etc) is that the "RUN" capacitor needs to be replaced. When a "START" capacitor fails it is easy to determine as the A/C will not start, however when a run capacitor goes bad, the result is that the unit will pull higher amps if it is able to continue running. If the Tech didn't believe 17amps was a concern, I doubt he would have pulled and tested the capacitors, however imo he should have done so.

Here is one link just for fyi (not sure if it is for your A/C) but notice in the description:
If your run capacitor goes bad, the motor can turn on but the running amperage will be higher than normal, causing the motor to run hot and have a short life expectancy.

https://www.rvupgradestore.com/Colem...-p/70-4144.htm
__________________
2010 GreyHawk 31SS
craigav is offline   Reply With Quote
Old 08-07-2022, 05:30 AM   #16
Junior Member
 
Join Date: Jul 2022
Location: Arcadia
Posts: 8
Thanks for the capacitor info. Sure beats the price of a new A/C if that’s the issue. BTW, our surge protector at the post indicates 124V and 17-18 amps. I’ll look into what it would take for me to replace the capacitor. If too involved I’ll get the tech back out to do it. Thanks again.
jramsey2008 is offline   Reply With Quote
Old 08-07-2022, 07:27 AM   #17
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 3,600
Quote:
Originally Posted by jramsey2008 View Post
Thanks for the capacitor info. Sure beats the price of a new A/C if that’s the issue. BTW, our surge protector at the post indicates 124V and 17-18 amps. I’ll look into what it would take for me to replace the capacitor. If too involved I’ll get the tech back out to do it. Thanks again.
A word of CAUTION to share is that a capacitor can contain a lot of electricity in it even after the power is off, you should use an insulated screwdriver across the capacitor terminals to short out the capacitor's terminals in order to remove any residual electricity stored in it prior to touching any of the terminals on the capacitor. Other than that, it is relatively easy to replace.

The voltage you referenced is fine as you suspected earlier.

One other thought, is that if the entire RV is pulling 17~18 amps, then maybe the A/C is pulling less than 17a as usually a few amps are flowing to the converter and other items even when everything else appears to be turned off.

So if you had 14~15a going to the A/C and 3~4a elsewhere, that wouldn't be uncommon. But if the A/C by itself is pulling 17~18a then that would be more than expected where replacing the run capacitor should lower the A/C compressor's amp draw and will lower the running amp draw if the run capacitor is bad. ~CA
__________________
2010 GreyHawk 31SS
craigav is offline   Reply With Quote
Old 08-10-2022, 03:18 PM   #18
Senior Member
 
Wireman's Avatar
 
Join Date: Dec 2015
Location: Murrieta
Posts: 690
I would be troubleshooting why the cooling fan isn't working.
Wireman is offline   Reply With Quote
Old 08-10-2022, 03:28 PM   #19
Senior Member
 
craigav's Avatar
 
Join Date: Mar 2017
Location: North Texas
Posts: 3,600
Quote:
Originally Posted by Wireman View Post
I would be troubleshooting why the cooling fan isn't working.
Keep in mind that the cooling fan is for the charge\power converter, not for the 120v breaker panel even though it is in the same area. The cooling fan is thermostatically controlled by the converter's operating temp, not the breakers operating temp. ~CA
__________________
2010 GreyHawk 31SS
craigav is offline   Reply With Quote
Old 08-11-2022, 11:27 AM   #20
Junior Member
 
Join Date: Dec 2019
Location: Miami
Posts: 2
Ac on 20 ???

Quote:
Originally Posted by jramsey2008 View Post
I know the connections on the A/C breaker (20/15 combo) are tight, as replacing that breaker was my first step. When the new breaker tripped I noticed that all were hot. I’ll be replacing the single 15 amp breaker tomorrow (it seemed to be the hottest, though that could just be my imagination), and will recheck all connections then.
I've been rving since 1971. In my early days I burned out several AC compressors trying to run them on a 20 amp circuit. If you're going to insist on attempting to run an AC on only 20 amps you have to monitor your ac voltage at any Outlet inside your rv. If the voltage goes below 106 volts ac the AC compressor is drawing lots and lots of current and overheating and will eventually fail as is the entire 20 amp circuit.
JOLOOOTE is offline   Reply With Quote
Reply

Tags
a/c breaker, tripping


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 07:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.