RE: 2014 Seneca Super C 37TS. AC outlets do not work either while on generator or 30 amp land hookup. The bathroom outlet with surge protector is also not active and will not be reset. The fuses at the bedroom all look good. Are there any other hidden fuses to check??
|
The common elements of shore and generator power are the transfer switch and circuit breaker panel. No fuses will be involved with 120 volts as that is protected by circuit breakers.
I would check the transfer switch first. Do this without any power applied (not plugged in and generator off). Remove the box cover and look for loose or burnt connections. Problems here are not that uncommon so it is a good place to start.
The transfer switch will feed the circuit breaker panel's main 30 amp breaker. To really verify where the voltage is being lost will require a voltmeter. But, if you are not comfortable measuring 120 volts DON'T DO IT. This can be a lethal voltage if you get across it. You may need an electrician to look at things.