Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
Jayco RV Owners Forum
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 12-04-2022, 09:44 AM   #1
Junior Member
 
Join Date: Jun 2022
Location: Cleveland
Posts: 12
Shore power question.

Why would the 30 Amp breaker outside on the power pole trip (shore power) but no the main 30amp breaker inside the TT? It’s only happened twice and both times the A/C was full blast.

If we pulled more than 30 amps between the A/C and the other outlets/water heater/fridge, why didn’t the inside breaker pop? Thanks for any info!

2022 Jayco SLX8 26RLS
THyatt123 is offline   Reply With Quote
Old 12-04-2022, 09:57 AM   #2
Senior Member
 
Grumpy's Avatar
 
Join Date: Nov 2011
Location: Where ever the boss says we're going.
Posts: 13,617
Because that was the weakest link. Breakers do wear out/weaken, especially if turned off and on regularly which is what happens at the power post.
__________________
DISNEY LOVERS
Grumpy is online now   Reply With Quote
Old 12-04-2022, 09:58 AM   #3
Junior Member
 
Join Date: Jun 2022
Location: Cleveland
Posts: 12
Quote:
Originally Posted by Grumpy View Post
Because that was the weakest link. Breakers do wear out/weaken, especially if turned off and on regularly which is what happens at the power post.
Sounds like a conversation is to be had with the campground. Thank you for such a quick response!
THyatt123 is offline   Reply With Quote
Old 12-04-2022, 10:04 AM   #4
Junior Member
 
Join Date: Aug 2022
Location: Fort Wayne
Posts: 2
Examine your power cable & trailer side cleaning what you can.
GEPrice is offline   Reply With Quote
Old 12-04-2022, 10:33 AM   #5
Senior Member
 
Join Date: Dec 2020
Location: South Brunswick
Posts: 206
Quote:
Originally Posted by Grumpy View Post
Because that was the weakest link. Breakers do wear out/weaken, especially if turned off and on regularly which is what happens at the power post.
Agree with above but also say that the breaker inside of your rig should be exercised occasionally as well. Have seen them stick over the years from never being moved.
__________________

2015 Starcraft AR-ONE Maxx 21FB
2019 Chevrolet Suburban LT 1500
mrmom is offline   Reply With Quote
Old 12-04-2022, 11:06 AM   #6
Senior Member
 
Join Date: Mar 2017
Location: North Texas
Posts: 2,171
While a circuit breaker can wear out with time and especially with multiple trips on the breaker, there is still yet another reason why the pedestal 30a breaker often breaks before the 30a main inside the RV.

The reason is that a common breaker works by two different methods, first being magnetic and if a large amount of power flows through the breaker, the breaker trips due to the increased magnetism, the second method and the one of relevance here is the "thermal" trip where as the temp inside the breaker increases due to the load and with time, the breaker will trip due to the thermal (heat) increase inside the breaker.

What happens is that as power flows through the breaker, heat is generated. When that heat is high enough for a long enough time (greater or equal to 80% of the breakers rating) then the breaker will trip. The thermal aspects are sensitive to the ambient temperature that the breaker exists in. So, with two fully functional breakers at the same rating (30a in this case) once you exceed about 24a (80%) with a continuous load then the breaker in the warmest location will break prior to the breaker located in the cooler location (there are curve charts regarding load and time to break). This often means and in particular during the summer months that the pedestal breaker breaks first being in the hot ambient temp vs the breaker inside the RV being in an air conditioned environment in most cases (even if there isn't much air flow in the breaker panel, often that location is cooler than inside the pedestal).

btw, just the opposite would occur in the winter, if you had electric heaters that pulled more than the 24a continuously, with time the interior breaker would trip prior to the breaker located at the pedestal which would be in a colder environment.

Most of what I am saying here is rarely noted, as the condition only occurs when the load is right there at the maximum breaker rating for current and the pedestal breaker is warmer than the RV main breaker. A standard breaker can hold 80% continuous of its rating for 3 hours. 100% non-continuous, and a curve in time between 80 and 100% where more than 80% reduces the time to trip, but is certainly not an instant trip (from minutes into about 3 hours). ~CA

btw, what I am sharing here is not specific to 30a breakers, same would be for all common breakers as well.
__________________
2010 GreyHawk 31SS
craigav is offline   Reply With Quote
Old 12-04-2022, 12:01 PM   #7
Senior Member
 
Join Date: Jun 2016
Location: Newburgh
Posts: 5,197
Quote:
Originally Posted by craigav View Post
While a circuit breaker can wear out with time and especially with multiple trips on the breaker, there is still yet another reason why the pedestal 30a breaker often breaks before the 30a main inside the RV.

The reason is that a common breaker works by two different methods, first being magnetic and if a large amount of power flows through the breaker, the breaker trips due to the increased magnetism, the second method and the one of relevance here is the "thermal" trip where as the temp inside the breaker increases due to the load and with time, the breaker will trip due to the thermal (heat) increase inside the breaker.

What happens is that as power flows through the breaker, heat is generated. When that heat is high enough for a long enough time (greater or equal to 80% of the breakers rating) then the breaker will trip. The thermal aspects are sensitive to the ambient temperature that the breaker exists in. So, with two fully functional breakers at the same rating (30a in this case) once you exceed about 24a (80%) with a continuous load then the breaker in the warmest location will break prior to the breaker located in the cooler location (there are curve charts regarding load and time to break). This often means and in particular during the summer months that the pedestal breaker breaks first being in the hot ambient temp vs the breaker inside the RV being in an air conditioned environment in most cases (even if there isn't much air flow in the breaker panel, often that location is cooler than inside the pedestal).

btw, just the opposite would occur in the winter, if you had electric heaters that pulled more than the 24a continuously, with time the interior breaker would trip prior to the breaker located at the pedestal which would be in a colder environment.

Most of what I am saying here is rarely noted, as the condition only occurs when the load is right there at the maximum breaker rating for current and the pedestal breaker is warmer than the RV main breaker. A standard breaker can hold 80% continuous of its rating for 3 hours. 100% non-continuous, and a curve in time between 80 and 100% where more than 80% reduces the time to trip, but is certainly not an instant trip (from minutes into about 3 hours). ~CA

btw, what I am sharing here is not specific to 30a breakers, same would be for all common breakers as well.
Very well stated Craig - Thank you! I can't send thanks from my phone....
Marcm157 is offline   Reply With Quote
Old 12-04-2022, 03:45 PM   #8
Junior Member
 
Join Date: Jun 2022
Location: Cleveland
Posts: 12
You done learnt me something, lol. I appreciate the thorough explanation. Makes perfect sense.
THyatt123 is offline   Reply With Quote
Old 12-04-2022, 03:54 PM   #9
Site Team
 
JFlightRisk's Avatar
 
Join Date: Apr 2012
Location: Newark, NY
Posts: 13,655
Excellent explanation craigav! Thanks, I wasn't aware of the two ways they trip. You get an 'attaboy'!
__________________
Moderator
Every day's a learning experience, though sometimes not what we expected.

2012 Jay Flight 19RD
2016 Ford F150 XLT 2X4 SC 3.5L Eco Max Tow
2010 Tundra TRD DBL Cab (Traded)
2 new fluffy Corgis, Bayley and Stanley
JFlightRisk is offline   Reply With Quote
Old 12-04-2022, 03:57 PM   #10
Junior Member
 
Join Date: Jun 2022
Location: Cleveland
Posts: 12
Smile

Quote:
Originally Posted by JFlightRisk View Post
Excellent explanation craigav! Thanks, I wasn't aware of the two ways they trip. You get an 'attaboy'!
Agreed. I will have to admit other forums (not RV related), it feels like people are just waiting to pounce on someone for asking a question. I always appreciate someone genuinely willing to help and share information. 🙏🏻
THyatt123 is offline   Reply With Quote
Old 12-04-2022, 04:08 PM   #11
Site Team
 
JFlightRisk's Avatar
 
Join Date: Apr 2012
Location: Newark, NY
Posts: 13,655
Quote:
Originally Posted by THyatt123 View Post
Agreed. I will have to admit other forums (not RV related), it feels like people are just waiting to pounce on someone for asking a question. I always appreciate someone genuinely willing to help and share information. 🙏🏻
Thanks, that's what makes the JOF a family friendly place. All of the moderators here take great pride in what we do, and anti-pouncing was one part of our exhaustive and highly intense training. Ok, that's not entirely accurate, but there was a lot of it. We love what we do.
__________________
Moderator
Every day's a learning experience, though sometimes not what we expected.

2012 Jay Flight 19RD
2016 Ford F150 XLT 2X4 SC 3.5L Eco Max Tow
2010 Tundra TRD DBL Cab (Traded)
2 new fluffy Corgis, Bayley and Stanley
JFlightRisk is offline   Reply With Quote
Old 12-04-2022, 07:08 PM   #12
Senior Member
 
SloPoke's Avatar
 
Join Date: Apr 2016
Location: Kingman AZ and where our Seneca is today.
Posts: 2,956
Quote:
Originally Posted by craigav View Post
While a circuit breaker can wear out with time and especially with multiple trips on the breaker, there is still yet another reason why the pedestal 30a breaker often breaks before the 30a main inside the RV..
Well described,

But OP still should look for any faults in the power cord / connectors / connections to the main RV panel. The power pedestal breaker is protecting everything past the breaker, that could be the pedestal 30A receptacle as well as the entire cable/RV connected to it.
__________________
Steve & Stacy with Jasper (Australian Cattle dog)
2015 Seneca 36FK
Custom 27' flatbed trailer hauling:
07 Toyota FJC & Yamaha Kodiak 400 ATV

SloPoke is offline   Reply With Quote
Old 12-04-2022, 07:09 PM   #13
Junior Member
 
Join Date: Jun 2022
Location: Cleveland
Posts: 12
Gotcha, I appreciate it!
THyatt123 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Powered by vBadvanced CMPS v3.2.3
Disclaimer:

This website is not affiliated with or endorsed by Jayco, Inc. or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 08:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2023, vBulletin Solutions, Inc.
Copyright 2002-2016 Social Knowledge, LLC All Rights Reserved.